Dell PowerEdge 1920W UPS Network Management Card

Hi,


We have recently bought a PE 1920W rack mount UPS and have installed the network management card however I cannot seem to access the this via the Dell software or through the COM port.

I have both network cables plugged in, one going to the COM port on my desktop from the settings port on the UPS and the other into a switch. When I use Putty or similar, nothing loads, just a blank screen.

Has anybody come across this before or am I doing something wrong?


Thanks

  • Daniel My

    12 Elder

    •

    6204 Posts

    3106

    1

    Posted May 4th, 2013 10:00

    Yes, theres only 1 COM port. I've also tried using the COM port on our server (T620) and I get the same blank screen. All the settings are correct (9600, 8 bits, no parity, 1 stop, no flow)

    You may have a bad cable. There are only 3 possible issues I can think would cause this bad cable, wrong COM port, or a faulty NMC. Do you have a serial port on these systems, or are you using come kind of serial to USB converter? Also, by your answer it does not sound like you understood what I was saying about the communication port. COM ports are logical not physical ports. I see that you are using COM1, have you gone into device manager to verify that the serial port the cable is attached to is assigned COM1 and not COM5 or some other COM port? The most likely issue would be that you are using the wrong COM port to connect, but it could be one of the other issues I listed. The only way to rule them out would be to try a known good cable or a known good NMC.

    Thanks

  • Daniel My

    12 Elder

    •

    6204 Posts

    3106

    0

    Posted May 2nd, 2013 12:00

    Hello tombullockoel

    It should be fairly straight-forward. Are you sure that the COM port you are using is the serial port that the management cable is attached to? I would suggest trying the other communication ports to see if they allow the connection. Also, make sure putty is set to 9600 baud, 8 data bits, no parity, 1 stop bit, no flow control.

    Thanks

  • 3106

    0

    Posted May 3rd, 2013 02:00

    Yes, theres only 1 COM port. I've also tried using the COM port on our server (T620) and I get the same blank screen. All the settings are correct (9600, 8 bits, no parity, 1 stop, no flow)

  • CT11

    2 Posts

    3106

    0

    Posted May 4th, 2013 08:00

    Once you have your putty window up, have you tried hitting enter a few times?

  • 3106

    0

    Posted May 9th, 2013 05:00

    Daniel - It was using a different COM port (2), thanks for your help on that.

    Would I be correct in saying the NMC or the Local/Multi Node Manager will tell each machine connected to power down if a given criteria is met?

  • Daniel My

    12 Elder

    •

    6204 Posts

    3106

    0

    Posted May 9th, 2013 10:00

    Glad to hear you got it figured out!

    You can use ULNM or MUMC to set power down criteria on the servers. MUMC is more of a central monitoring/management utility for managing multiple UPSs, so ULNM would probably be what you want. You can read more about them and download them here: http://www.dellups.com/support_download.asp 

    Thanks

  • 3106

    0

    Posted July 2nd, 2013 01:00

    If the ULNM software is running on a Hyper-V server, is there a way to tell the VM's to power down if the power criteria is met? Or would I have to install the ULNM software on each VM?

    Thanks