Dell R730xd 100% loud fan speed even with server room at 20 C/68 F temperature

Server room is 68 Fahrenheit or 20 Celcius and yet the dell R730xd server is running fan at 100% loud as hell

the 2 CPU are E5-2640 v4 90 watts CPU and have a mellanox connectx-5 2 x 100G network card and only 3 drives populated of the 12 drives slots and 2 x reade OS drives

why is the fan running at 100% and how do i fix this?

Please see screenshots below

https://imgur.com/D7qKReL

https://imgur.com/lcm4Ljt

https://imgur.com/PegigfI

  • DELL-Erman O

    Moderator

    •

    2984 Posts

    •

    14874 Points

    0

    0

    Posted October 30th, 2024 10:50

    Hello,

    I think, it appears that your server’s fans are operating at maximum speed due to the presence of the Mellanox ConnectX-5 network card. Dell servers often increase fan speeds when they detect non-Dell components to ensure adequate cooling. Please check your BIOS, iDRAC, and other firmware are up to date. This can sometimes resolve fan speed issues. Sometimes, a simple restart of the iDRAC can reset the fan control logic. Check your CPU usage to ensure it is not excessively high, which could be causing the fans to run faster. 

      • Enable SSH on your iDRAC.
      • Connect to it and execute the following commands:
        racadm set system.thermalsettings.FanSpeedOffset 255
        racadm set system.thermalsettings.ThirdPartyPCIFanResponse 0
        racadm set system.thermalsettings.ThermalProfile 2
        

    I believe these steps should help get your fans under control. 

    Hope that helps!

    DELL-Erman O

    Social Media and Communities Professional

    Dell Technologies | Enterprise Support Services

    #IWork4Dell

    Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!