Replaced IDSDM module in R630 and no longer see redundancy
I've got a PowerEdge R630 running esxi 6.0. One of the IDSDM modules failed and it was clearly noted in iDRAC. This is the 'before' picture:
We swapped out the SD1 module. As it was booting, I was prompted to overwrite the new SD card in Slot 1 (or whatever the verbiage was). I entered ‘y’ at the prompt in the bios to confirm and it appeared to rebuild and eventually loaded the esxi OS. That part was good.
Now, the main page in the iDRAC shows all green, but when I view the flash media in the DRAC, I no longer see the redundancy or both SD modules listed. This is the 'after' picture:
This is a working system and it is difficult to get someone on-site or squeeze in any opportunities to reboot or shut it down.
Can you reboot iDRAC and check the behavior. If it is not resolved the issue you can remotely reboot the server using iDRAC and check whether iDRAC is showing IDSDM details.
Can you also check whether you have latest FW on IDSDM and iDRAC?
You can login to iDRAC and on Summary page you can find an option to Reset iDRAC under "Quick Launch Tasks" section. Resetting iDRAC will not impact or reboot server.
For IDSDM rebuild we need to reboot server. I also recommend to reinsert SD card and try.
This looks strange. You can try reseat of IDSDM and see whether it will resolve the issue. If that not fix the issue you can try updating iDRAC and BIOS first then later IDSDM
Tomorrow I will be able to try reseating the SD card. In the meanwhile I have just updated the iDRAC firmware so it is the latest. (The IDSDM still shows as both having failed).
Initially we were able to boot into the OS with SD1 as primary and the mirroring disabled. We were also able to boot into the OS with SD2 as primary and the mirroring disabled. But the entire time we never saw both SD cards show up in the iDRAC. And occasionally we would see one SD card show up but always in a failed state.
I have updated the BIOS and iDRAC/lifecycle controller firmware. I don't think that the IDSDM firmware update was successful because it still reads 0.15.
Now we get these:
I have migrated the live VMS off of this system and put the host in maintenance mode so I can at least work on it whenever we need too.
DELL-Shine K
6 Operator
•
3042 Posts
3310
0
Posted January 31st, 2021 18:00
Can you reboot iDRAC and check the behavior. If it is not resolved the issue you can remotely reboot the server using iDRAC and check whether iDRAC is showing IDSDM details.
Can you also check whether you have latest FW on IDSDM and iDRAC?