UNSOLVED

dthielheim

updated

11 years ago

0

55671

September 11th, 2015 01:00

Battery selftest not starting in 2700 UPS

Hi all,

hopefully this is the right place for the following question:

Followed the instructions in the user guide for manuall initiating a ups battery test, but nothing happens - control menu, battery test, schedule battery self test:yes...

Would like to do this because i believe, that the automatical self test after battery replacement didn't work.

UPS Status in the NMC states: "battery Charge Level: resting" and "battery Status: aborted".

Any help or hint is highly appreciated!

Regards, David

  • 1882

    0

    Posted September 28th, 2015 00:00

    Nobody, who can give me a hint regarding this issue?

    Regards, David

  • 1882

    0

    Posted April 27th, 2016 09:00

    Battery self-test requires the load on the computer to be (I believe) greater then 15% and the battery full charged in REST mode. If the load is less than 15% OR the battery is not in REST then battery self-test will not initiate.