Replaced Standby Power Supply Still Shows Faulted

I have a CX300 that has a faulted Standby Power Supply. I replaced the Standby Power Supply with a new one but it still shows that it is faulted in Navisphere and in Unishpere. Is there anything else I need to do to the system besides replacing the faulted hardware or did I get defective replacement hardware?

Thanks!

  • kelleg

    6 Operator

    •

    4537 Posts

    3567

    1

    Posted April 5th, 2013 14:00

    Try removing the sense cable from the back of the SP, then reboot (turn off the power on the SPS) and while it's booting, plug the cable back in. We've seen some issue where the IEEE serial port on the back of the SP gets locked up and won't work any more until you power cycle the SP.

    glen

  • mykul_71

    34 Posts

    3567

    0

    Posted April 9th, 2013 07:00

    Thanks for the suggestion. I tried what you said but now in Navishpere it has an error stating that Cabling Status is Unknown. Does that mean the serial cable is bad and should be replaced?

  • AnkitMehta

    4 Apprentice

    •

    1365 Posts

    3567

    0

    Posted April 9th, 2013 07:00

    If you've already tried the above step suggested by Glen, try reseating SPS Sense Cable one more time then restart the management server for both the SP's  If this doesn't clear the error "Cabling Status Unknown' replacing Sense Cable will be the next feasible step.

  • mykul_71

    34 Posts

    3567

    0

    Posted April 9th, 2013 07:00

    I am not an expert with this hardware, how would I restart management server for the SP's?

  • mykul_71

    34 Posts

    3566

    0

    Posted April 9th, 2013 08:00


    Thank you, I will try that next.

  • AnkitMehta

    4 Apprentice

    •

    1365 Posts

    3566

    0

    Posted April 9th, 2013 08:00

    Please, refer toHow to restart the Management Server for step by step instructions.

  • Madhug1

    2 Intern

    •

    127 Posts

    2265

    0

    Posted April 9th, 2013 10:00

    Hi,

    Verify the TLA part number of new SPS with the old one.

    It should be same. If it is different, contact EMC to get verified, if it is compatible with given model of the Array.

    Thanks

    Madhusudan

  • RRR

    6 Operator

    •

    5739 Posts

    2265

    0

    Posted April 11th, 2013 01:00

    in the past it happened to me several time that the SPS monitoring cable wasn't connected right. After reconnecting it the fault went away.

  • Allen Ward

    6 Operator

    •

    2124 Posts

    1012

    0

    Posted April 11th, 2013 11:00

    We just had an SPS on one of our CX4-240s replaced twice before Support said to wait until the SPS test cycle runs on the weekend. They believe that the error will go away as soon as the normal test cycle completes and verifies the new SPS.

    Has anyone else run across this before? I don't remember ever having to wait, but maybe this is something new with the CX4s. Or has it always been there and could be affecting this situation as well.

  • AnkitMehta

    4 Apprentice

    •

    1365 Posts

    1012

    0

    Posted April 11th, 2013 19:00

    IMHO, Why would one has to wait until the SPS test cycle i.e. Battery Testing?! One could do test the batteries manually as well. I do not agree with the above solution provided they have any hardware revisions which is backed up by a proper documentation or a Primus Article.

    glen Can you please, verify if EMC has any internal KB Article where it suggests this?

    As you mentioned you have 2 SPS replacement for the same storage system and it still did not clear the fault/error. Here is something which I can suggest with out SP Collects Analysis: (Sorry, believe it or not even for single HDD failure I analyze/insist SP Collect analysis and most of the time end up with correcting hidden issues too)

    - Verify the LED on the SPS.

    - Reseat SPS

    - Reseat Sense Cable

    - Replace Sense Cable if Required

    - Restart both the management servers together.

    - Still no joy then, you might need to reboot the SP of the SPS showing faulted/cabling status unknown.

    Only reason, I do not agree with the Support Resolution is, if the SPS is actually faulted and if you wait for an initial cycle to run you are putting your storage system vulnerable to second SPS failure!