What is the racadm command to check psu redundacy iDRAC7 ?
Today I noticed one of my R620s had a Redundancy Policy in Power Supply Options of "Not Redundant"
I have separate circuits going to each PSU so it seems I would want that to be "Input Power Redundant".
In the racadm CLI guide I don't see any command to check the value of that setting and I have a few hundred servers I would like to verify that setting.
racadm>>get system.power.RedundancyPolicy A/B Grid Redundant RAC1248: The RACADM "System.Power" group will be deprecated in a future release of iDRAC firmware. The group attributes will be migrated to "System.ServerPwr". racadm>>get System.ServerPwr #ActivePolicyName= #ActivePowerCapVal=242 #PowerCapMaxThres=680 #PowerCapMinThres=468 PowerCapSetting=Disabled PowerCapValue=242 PSPFCEnabled=Disabled PSRapidOn=Enabled PSRedPolicy=A/B Grid Redundant RapidOnPrimaryPSU=PSU1 racadm>>
mondeep
30 Posts
6719
1
Posted October 1st, 2015 05:00
Hi Cameron,
You can check this attribute:
racadm help system.power.RedundancyPolicy
To set it to Input Power Redundant you need to run this command:
racadm set system.power.RedundancyPolicy 1
To view it after setting Redundancy policy to Input Power Redundant:
racadm get system.power.RedundancyPolicy
Regards,
Dell-Mondeep