How to configure Dell T710 with APC BackUPS XS1300 to boot after power failure
They're doing some serious remodeling in our building which means we've lost power twice in the last week...usually after hours. The UPS does a fine job in starting a graceful shutdown, but I want the server to boot up after the utility power is returned.
How do I configure this? Couldn't find anything in the BIOS...or iDRAC6...or Win2008.
Thanks for your quick reply. We made the change you suggested, and set the restart delay to 60s. While this gets us closer it doesn't solve the problem. Here's what we're observing:
Win2008 R2 server is up and running. Power profile is set to balanced. UPS is detected and accurately shows the charge %/minutes remaining.
We unplug the UPS. Windows detects this...and when the battery gets low, it performs a graceful shutdown.
We plug the UPS back in. The system does NOT boot.
Our hypothesis is that the BIOS never "sees" a power loss because Windows shuts down gracefully and the UPS battery is never depleted.
To test this hypothesis:
We turned the UPS off. All the lights on the server went out (network activity, et al).
Turned the UPS on.
The system started after the 60s delay.
It seems that the BIOS needs to see a complete power loss...which will never happen with a graceful shutdown.
What we really need is a BIOS setting that powers up the machine whenever a) it is off, and b) it has utility power. Is such a thing available and/or possible?
If you set the bios to "last", the last state as far as the bios is concerned is "off" as Windows did a graceful shutdown.
Have you tried setting the bios power setting to "on". This should force the server to power on any time it gets power (e.g. after a graceful shutdown and losing power completely and then power being restored).
There is one gotcha though; if power is restored before the battery was completely dead, the server may remain in an off state as the power never was completely lost.
Thanks for your suggestion. We are using the "on" setting, but we are trying to get around the "gotcha" you've described. The server does a graceful shutdown...which removes almost all load from the UPS...so the UPS battery never depletes and the server is never restarted.
Didn't get an official answer from them but I'd be surprised if it did. The BackUPS line is not really designed for servers, so the software they provide doesn't support Win2008 R2. I am relying on the built in support that Win2008 provides.
I was hoping that Windows would inform the BIOS and/or the UPS that the shutdown was "forced" by a low battery condition....and that it would power back on when line power was restored. Seems like such a simple, obvious thing, but I guess not.
Doug Clutter
1 Rookie
•
10 Posts
3089
0
Posted February 25th, 2011 09:00
Thanks for your quick reply. We made the change you suggested, and set the restart delay to 60s. While this gets us closer it doesn't solve the problem. Here's what we're observing:
Our hypothesis is that the BIOS never "sees" a power loss because Windows shuts down gracefully and the UPS battery is never depleted.
To test this hypothesis:
It seems that the BIOS needs to see a complete power loss...which will never happen with a graceful shutdown.
What we really need is a BIOS setting that powers up the machine whenever a) it is off, and b) it has utility power. Is such a thing available and/or possible?