I have 3 PowerEdge servers (2800, 2900, 1950) in a small server room with a portable cooling unit (A/C unit). Earlier today the A/C unit shut off for no apparent reason. As a result, the room temperature rises which in turn causes server fans to rev up.
The 3 servers generate so much heat in so little time. I came back from lunch and heard some noise from the server room (my office is next to the server room). It turns out the noise was coming from the server fans revving up at high speed. It's so loud that I can hear it from far away.
I opened up the server room. The room temp is about 100 degree Fahrenheit. No kidding. Everything in that room feels so hot; external tape backup units, switches, firewall, servers, racks etc. I am so glad it happens while I'm at work. If this happens during the weekend, it may lead to fire.
In a matter of seconds I turned the A/C back on, full blast. Everything is back to normal now.
I have Dell OpenManage Server Administrator version 5.2.0 installed. I am sure I can take advantage of this software to do the following when temp hits a certain threshold:
- warn me by email (my cell phone has an email address)
- shut down the server
etc
Can someone help me configure Dell OpenManage to do the above or perhaps to do a better job in handling this situation?
Thank you
note:
Forgot to mention that there is no warning or errors in Windows Server 2003 event logs. I think that is odd. Dell OpenManage should have (at least) left warning messages in the logs.
You could use OpenManage IT Assistant (ITA) in conjunction with OpenManage Server Administrator (OMSA) to achieve all of this (sending e-mail, taking specific actions when something goes wrong in a server etc).
You already installed OMSA on each server, that is correct. Now you can configure various thresholds (like voltage, temperature, Fan RPM) in OMSA for each of the system. This is used to configure OMSA to generate alerts (e.g. if a fan rpm increases over
nnnn RPM, generate a warning SNMP trap).
Additionally, install IT Assistant on one of your systems (need not necessarily be one of these servers). It could be any system from where you will monitor these 3 servers. Create a
Discovery Range in ITA to discover all of the devices that you wish to manage (servers, client systems, storage, printers etc). Configure appropriate protocols to manage these devices (servers are commonly managed by SNMP). ITA user's guide provides details about this.
Once ITA has discovered and classified these under Servers, configure SNMP so that each of the managed servers can send SNMP alerts to the ITA system. You could view them under
Alert->
Logs in ITA (or for each device, it is available on the right side in the main devices view). ITA can take specific actions on these alerts - like email or execute a custom script etc. To do this create appropriate
alert action filter to select which type of traps you would like ITA to work upon. Then create an
Alert Action as per your requirement.
Note: ITA has a web-based interface, so you can remotely access it from a browser.
The following link provides many tutorials, which will help you to configure OMSA and ITA, configuring SNMP, email alerts in ITA etc.
By the way, I notice OMSA has "Thermal Shutdown" feature. I suppose I can enable this feature to shutdown the server when temperature exceeds warning (or failure) threshold. Will this work? Does this feature shutdown Windows Server 2003 OS and running applications?
I also notice under (OMSA) Alert Management (tab) - Platform Events (sub tab) - Temperature Probe Warning, we can check "Power Off System" to shutdown the system. I understand that this is a dirty shutdown (doesn't shutdown OS and running applications). What's the difference between this and Thermal Shutdown option? Do they work independently of one another?
I realized that using IT Assistant to send me email alerts (when there's temperature problem) won't do any good. I can only know it's happening. If I get the alert while 'm away from work (during weekends), there's nothing much I can do. Even if I can come to the office on weekends, I won't make it in time (it takes at least 30 minutes to drive to work). By then the server temperature would be too darn high.
Therefore, I'm setting my priority on configuring server auto shutdown when temperature hits max threshold. If I can set OMSA to do auto shutdown (preferably OS + applications shutdown), that'll be great. Any tips would be appreciated. Thanks much.