xiazhen

updated

14 years ago

X

xiazhen

1 Rookie

•

44 Posts

0

3808

September 1st, 2011 20:00

how to configure RecoverPoint with VNX5300

hi,all:

  following my envirment.

  four RPA, two VNX5300, two san witch.  my plan is construct to CRR .

  at site 1 , two RPA, one VNX5300, two san switch. firbrac connect with san switch.

  at site 2  two RPA, one VNX5300.    RPA to VNX5300 is directly  connecting.

my question,

1. frabric cable connection type.

     can i do from the VNX5300 SP to RPA ?

2.  do the VNX5300 need to install splitter enabler ?

best regards

  • heidistor

    9 Posts

    666

    0

    Posted September 2nd, 2011 11:00

    I just set up the same config last week, except w/o SAN switches as this is an iscsi fabric

    1)  I direct attached two SP ports on each SP to each RPA at each site.   There is a picture, although, not a great one in the Recoverpoint procedure generator.

    2) I did install the splitter enabler and it worked fine.

  • SKT2

    2 Intern

    •

    1340 Posts

    666

    0

    Posted September 2nd, 2011 17:00

    Any chance you know if this vnx(5100,5300) supports both FCAL and P2P topology?

  • 666

    0

    Posted November 24th, 2011 18:00

    Hello,

    Thank you for contacting EMC.

    Yes, I do have seen with couple of customers and they have implemented with both FCAL and P2P.

    Regards

    Suresh Thirumalaisamy


    Suresh Thirumalaisamy

    Technical Support Engineer

    Worldwide Technical Support - IMG RecoverPoint

    Office Hours: Sun-Thur, 20:00 to 05:00 hrs EST

    Phone : (US Tollfree)1-800-782-4362 || Extn 7633381

    Email : Suresh_Thirumalaisamy@emc.com

    Please let us know what you think of the level of service provided by sending an email to my manager,

    Vashisht, Mohit @ (Mohit.Vashisht@emc.com)

  • VDA_TECH

    1 Message

    666

    0

    Posted April 9th, 2013 09:00

    hi will you please help me in getting Recoverpoint procedure generator.

    Thanks in advance.