I have two r720s BOTH have developed an issue where Fan 4 keeps running even when the system is off. One system has iDrac FW 2.65.65.65 and the fan stays on very low speed, the other FW 2.63.60.62 and the fan is always at full blast, system on or off.
The second system was purchased in order to fix the issue of the first with a MB swap. But it too developed this problem - on the same fan - after updating the FW to current.
I have read 1 other post here with the same problem, their solution being to revert to a much older (v1) FW. The fact I have 2 systems displaying an identical issue on the same fan seems to confirm it is the FW.
I realise these are older systems but can anyone at Dell offer some insight regarding which FW is recommended to fix this issue? 2.65.65.65 is the last for the r720 I believe - perhaps there is some other driver or combination of bios & FW that will stop these errant fan 4s?
System 1 - FW 2.63.60.62, bios 2.9.0 (Fan 4 full blast at all times)
System 2 - FW 2.65.65.65, bios 2.4.3 (Fan 4 on low speed after system is off)
OK - I have fixed the problem. It does seem to be a Firmware issue**. Specifically some firmware after 2.40.40.40.
To recap:
System 1 - Fan 4 always on full speed. - 2.63.60.62, bios 2.9
System 2 - Fan 4 always on, very low speed. - 2.65.65.65, bios 2.4
System 2 was originally upgraded from a v1 FW, walking through a few versions including 2.40.40.40 then directly to 2.65.65.65, I wasn't sure but I didn't notice the fan being on low all the time until I updated to 2.65.65.65. That's when I started noticing it.
So I rolled it back to 2.40.40.40 - the low speed fan 4 has stopped!
Next, as recommended, I updated system 1 (with the full speed fan 4) from 2.63.60.62 to latest 2.65.65.65. No change.
So I downgraded system 1 to 2.40.40.40 - this FIXED the fan 4 full speed issue.
Both systems are now on 2.40.40.40 and both are operating normally, system off = fans off. IDK exactly which FW causing the issue but it's between 2.40.40.40 and 2.63.60.62.
**(The complication is that System 1 was once running normally with 2.65.65.65 - the high speed fan 4 was an issue that developed after that system had been off for some time)
I tried checking if there is any notes on such issue on R720 iDRAC version, but there is no known issue stated. There are a few things to I would like to check. Does Fan 4 spins after a few minutes of wait? What happen if the power cables are pulled and installed back, does the fan spin? When the system is off, are there any LED lid? If you were to swap Fan4 and Fan3, does the issue follow the slot? Do you have iDRAC access? Have you tried resetting the iDRAC?
DELL-Joey C
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’ if I did.
Can I know if the fan do stop in period of time, have you monitored that? like it spins for about 5 to 10 minutes? Has the other firmware in the server have been updated? eg: BIOS.
Reset of iDRAC, what kind of reset would it be? Have you tried RACADM hard reset?
Try this, remove all components except the below and the fans. Then try connect the power cable and check if fan 4 still spins:
•One Power Supply •Control Panel (for power button functionality) •Working cable connection between control panel and system board •One Processor (CPU) in socket CPU1 (minimum for troubleshooting) •One Memory Module (DIMM) installed in socket A1 •System Board •Backplane (for R720xd control panel connection)
DELL-Joey C
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’ if I did.
@jms99 , As @DELL-Stefan R mentioned some components (E.g. iDRAC, NDC) on the server will be running even if server is powered off. Some of the FANS will be running at low RPM for cooling of these components. This is dependent on the server configuration as well. I would recommend to update iDRAC FW to latest on system 1 also and check whether FAN running at low RPM after the upgrade.
The fan on both machines stay on constantly, it doesn't stop, 1 day later still on.
I think I must have only done a soft reset (via F2 menu, or Lifecycle Controller, can't recall which), I haven't used RACADM. I will try it, if that fails I'll try the troubleshooting steps you suggest.
I noticed the same issue today after updating my R720. With firmware 2.40.40.40 (after shutdown) the number 4 fan isnt powered up and spinning. After updating to the FW 2.65.65.65 it does spin. I also tried FW 2.63.60.62 same thing. All that running the latest BIOS (2.9.0)
Withing a minute of shutdown the number 4 fan starts to spin at low rpms. I tried changing No4 with No3 fan and various other combinations with the same result. I read the comment above that it may be for cooling of the idrac but this means that with FW 2.40.40.40 and before it wasnt needed? It seems like a firmware issue and ill revert back to 2.40.40.40 for now. If you can have a look please and maybe fix it? Thanks alot!
jms99
1 Rookie
•
5 Posts
3346
0
Posted March 11th, 2021 00:00
OK - I have fixed the problem. It does seem to be a Firmware issue**. Specifically some firmware after 2.40.40.40.
To recap:
System 1 - Fan 4 always on full speed. - 2.63.60.62, bios 2.9
System 2 - Fan 4 always on, very low speed. - 2.65.65.65, bios 2.4
System 2 was originally upgraded from a v1 FW, walking through a few versions including 2.40.40.40 then directly to 2.65.65.65, I wasn't sure but I didn't notice the fan being on low all the time until I updated to 2.65.65.65. That's when I started noticing it.
So I rolled it back to 2.40.40.40 - the low speed fan 4 has stopped!
Next, as recommended, I updated system 1 (with the full speed fan 4) from 2.63.60.62 to latest 2.65.65.65. No change.
So I downgraded system 1 to 2.40.40.40 - this FIXED the fan 4 full speed issue.
Both systems are now on 2.40.40.40 and both are operating normally, system off = fans off. IDK exactly which FW causing the issue but it's between 2.40.40.40 and 2.63.60.62.
**(The complication is that System 1 was once running normally with 2.65.65.65 - the high speed fan 4 was an issue that developed after that system had been off for some time)