SCv3000 health OK, but fault indicator still yellow flashing

Sorry for disturbance, is this enough to initaite the Service Request, or I ought to check something more in the SCv3000 storage? Now the DSM and Unicphere WEB-console reporting the storage health is OK, no unchecked/uncleared alerts. BUT, the 'fault indicator' still flashes yellow.

The system reported 'red alert' in DSM and Unisphere a day before, due to down state of a pair of server objects in 2 clusters (servers are physically down). To investigate that, I removed 'faulty' server objects using DSM (it will be OK to re-create these objects further), and confirmed all connectivity alerts. No more alerts remained after removing, but the front panel fault indicator remaining to alarm us about something unclear...

indicator_00.png

  

indicator_01_.png

  

indicator_02_.png

 

  • DELL-Sam L

    Community Manager

    •

    8151 Posts

    •

    34718 Points

    1688

    0

    Posted February 16th, 2021 10:00

    Hello polezhaevdmi,

    If your system is still under support I would open a service request so that we can look at your controllers and see what is going on.

  • DELL-Sam L

    Community Manager

    •

    8151 Posts

    •

    34718 Points

    1833

    0

    Posted January 28th, 2021 09:00

    Hello polezhaevdmi,

    If you select the alerts tab what alerts or errors are listed?  What is your current SCOS version?

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    1810

    0

    Posted January 29th, 2021 02:00

    Hello, Sam!

    System looks completely free of alerts now: even there are no connectivity alerts regarding switched off servers (gone during 2 last days).

    Regarding the SCOS version. System reports "7.4.21.4", but I remember I updated it from factory "7.4.21.4" to something like "Update 1" or "7.4.21.4.1" during deployment session about 1 month ago (as the update appeared available). Possibly, the version report displays 4 numbers only.

    PS> And yes, the fault indication - is still active, we checked this today again.

    IMG_20210129_114344_718_.png IMG_20210129_123022_397_.png

  • DELL-Sam L

    Community Manager

    •

    8151 Posts

    •

    34718 Points

    1791

    0

    Posted January 29th, 2021 11:00

    Hello polezhaevdmi,

    I would see if you can get a time to reboot your system & see if the error light comes back & it reports an error in the alerts tab.

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    1764

    0

    Posted February 2nd, 2021 01:00

    Thank You for advice, @DELL-Sam L !

    OK, it will require about up to 3-4 weeks to negotiate and perform the reboot, I will write the result. 

    And, to be accurate: Sam, please, confirm You're talking about complete procedure with storage "(stop production, indeed) -> shut down storage -> switch off PSU power -> remove AC cables -> wait for 2+ minutes -> re-seat AC cables back -> power on storage -> (start production, indeed)" (like here). Not the "soft reboot".

    Cheers!

  • DELL-Sam L

    Community Manager

    •

    8151 Posts

    •

    34718 Points

    1752

    1

    Posted February 2nd, 2021 09:00

    Hello polezhaevdmi,

    I would try & do the soft reboot first to see if it resolves your issue.  If it doesn’t resolve the error light, then you are going to do the shutdown and start process.

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    1731

    0

    Posted February 4th, 2021 05:00

    Hello, Sam!

    A lot of thanks, the Plan is clear (however, not simple: as to see the front panel one must go for ~500 meters and extra security point ), I will write the result in a couple of weeks.

    Cheers!

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    1698

    0

    Posted February 16th, 2021 02:00

    Hello again!

    Here are the results:

    - The 'soft reset' attempt vas in vain;

    - The 'complete hardware power cycle' was in vain too. Still the fault indicator flashes while web-console status is OK and no new alarms. I attached the summary screenshot again. In addition, we created a video-log of the system start process. The alarm indicator starts to be active at 04:40 time point approximately.

    timeline.png Summary_.png

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    1676

    0

    Posted February 17th, 2021 02:00

    Hello!

    Yes, Sam, the support for that system is active, I will continue with SR, and drop some information regarding result here. Great thanks for Your efforts!

  • polezhaevdmi

    1 Rookie

    •

    35 Posts

    629

    0

    Posted February 19th, 2021 02:00

    While waiting for SupportAssist files from first Customer, I eventially found another system with same effect. Different Company, different storage (SC5020F), different firmware - but effect looks the same. The common things among them I'm able to notice:

    - Both organizations have server cluster objects to provide the access to shared storage;

    - Both organizations had some servers connectivity lost, so, the cluster objects reported an alarm, which were propagated to storage level;

    - Both organizations solved the lost server warning (by reviving the server or removing unneccessary server object);

    - It appeared me, who visited both organizations and was asked 'why THAT blinks yellow?'.

    One SR is initiated, other one will be soon.

    frontpanel.jpg summary_.jpg