In my M1000e chassis with only 5 M610 servers, sometimes the fans rotates in abnormal high speed. Especially in the evenings. The temperature in the datacenter is 17 to 21 degrees always. The server temperature is stable at 22 degrees. I dont know what is the cause of this abnormal rotation. There is no FW updates, no health check warnings. The highest fan speed was 9125 and at the calm time it was 65xx.
Is there any way to find out what cause this behaviour?
AndreTheGiant
14 Posts
1365
0
Posted February 10th, 2014 03:00
How many power supply do you have and how are they configured (grid redoundancy)?
G11 server are not so energy efficient as the G12, maybe there is some peack in their usage?