Dell VRTX Sperc 2 Failed, Disks not accessible Backplane 1 SAS_2A, SAS_2B cable
is disconnected
Hello Folks,
I got the critical alerts on my Dell VRTX chassis listed below.
Chassis: The 12V storage voltage is outside of range
Chassis: The 12V FABB voltage is outside of range
Chassis: Power Supply redundancy is lost
perc-2 Backplane 1 SAS_2B cable is disconnected
perc-2 Backplane 1 SAS_2A cable is disconnected
perc-2 Chassis Integrated RAID 2 is no longer fault tolerant because the peer controller is not available.
Note: I have three blades M630 in my VRTX and none of them is connecting to Storage disks, I think due to failure of one perc controller, How can i enable the storage configuration to another perc controller which is available.
You can check the option in the CMC menu, I can't see it from here.
Log in to the CMC and got to Storage --> Controllers there you will see Fault Tolerant Mode if it shows Active/Passive it means one is active the other one will step in when there is an issue.
I checked the CMC log but there is no indication for the PERC failure, even the one that you mentioned is not listed there.
What I see is this:
Thu Aug 13 2020 10:34:06 The 12V Storage voltage is outside of range. Thu Aug 13 2020 10:34:05 The 12V FABB voltage is outside of range. Thu Aug 13 2020 10:34:04 Power supply 2 failed. Thu Aug 13 2020 10:34:01 Power supply 4 failed. Thu Aug 13 2020 10:33:59 Power supply 3 failed. Thu Aug 13 2020 10:33:59 Power supply 1 failed.
Was there a power outage or did someone power off the system around 10:33 and power back on at 11:13?
Except for these messages, all looks fine to me.
Reseating may solve the issue:
1. Open the system. 2. Check the storage controller card indicators. If the power indicator blinks irregularly or the attention indicator blinks amber, it indicates a fault condition. 3. Turn off the system and attached peripherals, and disconnect the system from the electrical outlet. 4. Reseat the integrated storage controller card, SAS cables, and the storage controller battery. 5. If the storage controller functions properly, close the system, reconnect it to the electrical outlet, and turn the system on. 6. If the storage controller does not function properly, log in to the CMC web interface and view the properties of the storage controller.
You may also check the Log via the CMC WebGUI like this:
To view the hardware logs using CMC Web interface, in the left pane, click Chassis Overview → Logs. The HardwareLog page is displayed. To save a copy of the hardware log to your managed station or network, click Save Log, and then specify a location for a text file of the log.
After you have stored a copy on your system, please clear the log and check if the system goes back to normal mode.
To clear the hardware log, click Clear Log on the CMC HardwareLog page in the WebGUI.
Looks likethere was a issue with the power before the PERC stopped working. We should check this one too, but here is some information about the sPERC.
There are two options on how to use the controller.
Opt. 1: Dual Fault Tolerant Shared PERC 8 Card Configuration
When the active controller stops functioning, the passive controller acts as a hot-spare and takes over the functions of the active controller.
Both controller cards are acting as single controller, no redundancy plan available.
The error messages you posted show that PERC-2 stopped working, so PERC-1 should take over. if the first option is active and the controller did not fail before.
Can you please check which policy is active 1 or 2 and also check the CMC log if there was an issue before with the first PERC. Here is an article that shows how to export the file:
what happend to PSU2? - The 12V FABB voltage is outside of range.
I'm thinking of the power plan you have, I see that there are 534Watts input at the moment, what kind of PSUs are installed? What I mean is, that there is maybe not enough power available in the system to run all the components.
thanks for all the log files. Power is out of the question, I see 4 1600Watt PSUs online in the power log. So you are good at this.
So we need to worry about the PERC-2. I haven't found any issue with PERC-1 this one should work - as your screenshot shows, it is green so it's healthy.
Is PERC-2 still listed under CMC -> Storage -> Controllers -> Troubleshooting? If yes, please Export the TTY Log for me.
You may also check the assignment of VD to the server, maybe this is not set correctly.
In CMC go to Storage -> Virtual Disk -> Assign, you will see a list of your VDs and how the single assignments are set.
DELL-Stefan R
Moderator
•
790 Posts
3078
0
Posted August 17th, 2020 01:00
Hi Arif.
You can check the option in the CMC menu, I can't see it from here.
Log in to the CMC and got to Storage --> Controllers there you will see Fault Tolerant Mode if it shows Active/Passive it means one is active the other one will step in when there is an issue.
I checked the CMC log but there is no indication for the PERC failure, even the one that you mentioned is not listed there.
What I see is this:
Thu Aug 13 2020 10:34:06 The 12V Storage voltage is outside of range.
Thu Aug 13 2020 10:34:05 The 12V FABB voltage is outside of range.
Thu Aug 13 2020 10:34:04 Power supply 2 failed.
Thu Aug 13 2020 10:34:01 Power supply 4 failed.
Thu Aug 13 2020 10:33:59 Power supply 3 failed.
Thu Aug 13 2020 10:33:59 Power supply 1 failed.
Was there a power outage or did someone power off the system around 10:33 and power back on at 11:13?
Except for these messages, all looks fine to me.
Reseating may solve the issue:
1. Open the system.
2. Check the storage controller card indicators. If the power indicator blinks irregularly or the attention indicator
blinks amber, it indicates a fault condition.
3. Turn off the system and attached peripherals, and disconnect the system from the electrical outlet.
4. Reseat the integrated storage controller card, SAS cables, and the storage controller battery.
5. If the storage controller functions properly, close the system, reconnect it to the electrical outlet, and turn the
system on.
6. If the storage controller does not function properly, log in to the CMC web interface and view the properties of the
storage controller.
You may also check the Log via the CMC WebGUI like this:
To view the hardware logs using CMC Web interface, in the left pane, click Chassis Overview → Logs.
The HardwareLog page is displayed.
To save a copy of the hardware log to your managed station or network, click Save Log, and then specify a location for a text file of the log.
After you have stored a copy on your system, please clear the log and check if the system goes back to normal mode.
To clear the hardware log, click Clear Log on the CMC HardwareLog page in the WebGUI.
Let me know the results.
Best regards,
Stefan