connecting poweredge to UPS

Hi we are going to add a Smart UPS 2200 to our four PowerEdge 2600 servers and need to to know the best configuration for this.  Our Poweredges have dual power supplies and each server has two AC cords coming from the back of each of the servers.  Do both of these cords connect to the UPS, or does one connect to the UPS and one go directly to the wall outlet?  Any ideas or debate would be appreciated.  Thanks in advance.
  • zkent

    30 Posts

    524

    0

    Posted July 25th, 2005 16:00

    You will want to connect all power cords to the UPS. You have 2 power cords on each unit because the server has 2 redundant power supplies. If one dies, the other can handle the entire load for the server. If a power supply were to fail you wouldn't want the remaining PS connected to a wall outlet which would leave it vulnerable to spikes and outages.

    If you are using a rack, you may need to purchase a PDU (power distribution unit) which is basically a fancy power strip that mounts inside your rack and connects to your UPS. The PDU gives your rack many outlets for connecting your devices and servers.