DD6300 fan speed increases every day for a short period of time
Hello,
I have a DD6300 (version 7.7.4.0-1017976), on which every afternoon around 15:45 the fan speed increases for 1 - 2 minutes. However, nothing has changed in the room environment and the cabinet is air conditioned.
Is there anything that can be configured? Has anyone had this problem?
Via CLI I could find out that the temperature (environment, drive IO) also rises for the moment.
7 o'clock in the morning: Enclosure 1 Fans Description Level Status ----------- ----- ------ FAN 0A low OK FAN 0B low OK FAN 1A low OK FAN 1B low OK FAN 2A low OK FAN 2B low OK FAN 3A low OK FAN 3B low OK FAN 4A low OK FAN 4B low OK FAN 5A low OK FAN 5B low OK ----------- ----- ------ Temperature Description C/F Status ----------------------- ------- ------ Ambient Temperature 19/66 OK SP Temperature 27/81 OK MP Temperature 19/66 OK CPU0 Temp Relative -45/-49 OK CPU1 Temp Relative -48/-54 OK Hottest HDD Temperature 28/82 OK Drive IO Temperature 42/108 OK DIMM Bank0 Temperature 28/82 OK DIMM Bank1 Temperature 28/82 OK DIMM Bank2 Temperature 28/82 OK DIMM Bank3 Temperature 28/82 OK ----------------------- ------- ------
15:45 in the afternoon, the speed goes up: Enclosure 1 Fans Description Level Status ----------- ----- ------ FAN 0A high OK FAN 0B high OK FAN 1A low OK FAN 1B low OK FAN 2A low OK FAN 2B low OK FAN 3A low OK FAN 3B low OK FAN 4A low OK FAN 4B low OK FAN 5A low OK FAN 5B low OK ----------- ----- ------ Temperature Description C/F Status ----------------------- ------- ------ Ambient Temperature 19/66 OK SP Temperature 27/81 OK MP Temperature 19/66 OK CPU0 Temp Relative -46/-51 OK CPU1 Temp Relative -48/-54 OK Hottest HDD Temperature 28/82 OK Drive IO Temperature 42/108 OK DIMM Bank0 Temperature 28/82 OK DIMM Bank1 Temperature 28/82 OK DIMM Bank2 Temperature 28/82 OK DIMM Bank3 Temperature 28/82 OK ----------------------- ------- ------
From about 15:47 the fan is down again. Enclosure 1 Fans Description Level Status ----------- ----- ------ FAN 0A low OK FAN 0B low OK FAN 1A low OK FAN 1B low OK FAN 2A low OK FAN 2B low OK FAN 3A low OK FAN 3B low OK FAN 4A low OK FAN 4B low OK FAN 5A low OK FAN 5B low OK ----------- ----- ------ Temperature Description C/F Status ----------------------- ------- ------ Ambient Temperature 20/68 OK SP Temperature 27/81 OK MP Temperature 20/68 OK CPU0 Temp Relative -45/-49 OK CPU1 Temp Relative -48/-54 OK Hottest HDD Temperature 28/82 OK Drive IO Temperature 42/108 OK DIMM Bank0 Temperature 28/82 OK DIMM Bank1 Temperature 28/82 OK DIMM Bank2 Temperature 28/82 OK DIMM Bank3 Temperature 28/82 OK ----------------------- ------- ------
It seems that the self-test was performed at the time the DataDomain was started. We restarted the DataDomain at a different time and thus the self-test was delayed.
Congrats! You have spotted the daily fan test schedule.
BIST Fan testing logic: The EOS fan test is an operational test that validates fan hardware. The firmware will perform the following actions to test the fans: Enable adaptive cooling test mode Configure the fan to run at its maximum PWM Wait for 30 seconds Validate the fan gets to within 15% of its defined maximum RPM speed Disable adaptive cooling test mode
Due to scheduled BIST (built in self test), Users may notice a high pitch whine due to the automatic fan validation tests.
This fan validation test is built into the BIOS FW. As part of the test cycle, the fans will operate at each speed (Low , Medium , High) to ensure that all fans are capable of sustaining full speed without failure. The test will complete in about 2 minutes.
bgrow1900
1 Rookie
•
4 Posts
791
0
Posted January 25th, 2023 05:00
It seems that the self-test was performed at the time the DataDomain was started.
We restarted the DataDomain at a different time and thus the self-test was delayed.
This is enough for us as a solution.