I have a datamover on my NS960 (5.6.47) that panicked and then the standby DM took over in about 2 minutes. I know it depends on what is going on with the datamover at the time. I'm curious to see what everyone is getting as far as the time for your datamover to failover to the standby and then how long does it take to fail it back to primary DM when you issue the restore. The CPU was probably around 10% when it panicked.
1- Did you check the logs on the data mover ? (using the command: "server_log server_2") to see what causes the panic .
2-To avoid this or to Prevent such event , You can check also some envrironment conditions in the datacenter (critical thermal events ,dust ...) that could impact on the Celerra .
3-You can Check your datamover, using some script for monitoring (CPU temperature /FAN speed ..)
4-Also check if there was some warnings in the datamover logs before the PANIC... It could help to understand what happened .
Possible cause:
Chassis over temperature. The storage system found internal temperature too high. It tries to correct an over temperature condition by increasing fan speed. Look for any obvious problems, such as obstruction of cooling vents or excessive room temperature.
If a panic happens on your primary Data Mover, you should be able to get the dump file from /nas/var/dump. There are, however, times when a Data Mover panics but does not produce a dump file. If this happens, you have limited options. The following example shows a scenario where you do have recourse.
Scenario:
Your primary Data Mover panics but does not fail over to the backup. Upon further research, you also find that the Data Mover did not produce a dump file. Here's what you do: Within the /home/nasadmin directory there is a file called downbox.sh. Run this script. The downbox.sh script will cause the box to panic again, this time producing a dump file. The script will also make the Data Mover fail over to the backup.
Note: Most likely sometime during this process you will be on the phone with EMC Support. Append to a text file all the preceding commands (with the exception of the downbox.sh) and send the text file along with the dump file to EMC. This can cut down on the diagnosis time considerably.
I'm laughing and also apologizing for the misunderstanding at the same time. My post was to see what other Celerra admins are experiencing as far as time is concerned when at datamover fails from the primary to the standby and fail back. How long does it take for the failover and then the fail back? Just curious what other people are seeing in the real world.
I just failed back to the primary tonight. The glitch was about 4 minutes, doubled the time it took when primary panicked and the standby kicked in. All of our NFS Oracle databases stay up without any problems during this outage duration. I believe the hard mounts on Solaris 10 are defaulted to 10 minutes, so we had some breathing room. Just wanted to share my experience.
so i just upgraded my NS80 to 5.6.49.301. All users were disconnected prior to the upgrade so support upgraded standby datamover first and then it was time to failover primary to standby. I have 960 mounts on this datamover (a lot of snapsures). It took 16 minutes for the CIFS/NFS services to come back online, i understand that if really had a datamover panic it would be much faster because there would be no graceful services shutdown process ...but still 16 minutes. There are new features in the DART code that supposed to reduce the time it mounts file systems so hopefully my next upgrade will be that faster.
The failover/failback time is purely "it depends" - on many things such as the number of file systems, shares and exports, replication sessions, checkpoints etc. Typically on a production environment it may be within 10 mins, but may be more as "dynamox" mentioned (I suspect a huge number of checkpoints contributed more here for "dynamox") - NFS mounts can sustain that but CIFS users may need to reconnect.
We had a situation where our NS960 panicked and failed over to standby. Although our NS960 was a target for replication, 2 minutes to fail it back seems about right. So, depending on the load, CIFS and FS, 4 minutes might be what your Celerra requires.
Failover times from a panic will differ from the failover times from manual failovers. The amount of time from a panic will also include a core dump being written to disk. And as described previously failover times will depend on Data Mover resource utilization (i.e. number and size of file systems, etc.).
Every system is different. In 5.6.47.x and later a new feature called fastmount was introduced which will mount file systems in parallel instead of serially as in the past.
junior6fr
8 Posts
845
0
Posted July 15th, 2010 16:00
Checklist:
1- Did you check the logs on the data mover ? (using the command: "server_log server_2") to see what causes the panic .
2-To avoid this or to Prevent such event , You can check also some envrironment conditions in the datacenter (critical thermal events ,dust ...) that could impact on the Celerra .
3-You can Check your datamover, using some script for monitoring (CPU temperature /FAN speed ..)
4-Also check if there was some warnings in the datamover logs before the PANIC... It could help to understand what happened .
Possible cause:
Chassis over temperature. The storage system found internal temperature too high. It tries to correct an over
temperature condition by increasing fan speed. Look for any obvious problems, such as obstruction of cooling vents or
excessive room temperature.
If a panic happens on your primary Data Mover, you should be able to get the dump file from
/nas/var/dump. There are, however, times when a Data Mover panics but does not produce a dump file. If this happens, you have limited options. The following example shows a scenario where you do have recourse.Scenario:
Your primary Data Mover panics but does not fail over to the backup. Upon further research, you also find that the Data Mover did not produce a dump file. Here's what you do: Within the
/home/nasadmindirectory there is a file calleddownbox.sh. Run this script. Thedownbox.shscript will cause the box to panic again, this time producing a dump file. The script will also make the Data Mover fail over to the backup.Note: Most likely sometime during this process you will be on the phone with EMC Support. Append to a text file all the preceding commands (with the exception of the
downbox.sh) and send the text file along with the dump file to EMC. This can cut down on the diagnosis time considerably.